Kevin W Holland
Member
- Location
- Naples-Bonita Springs, FL
I recently had a troubleshooting job where the AFCI was continually tripping multiple times per day. The AFCI cct was providing arc fault protection for the Msr Bed/bath ltg. All receptacles were connected together via "stab-in" method. After I had re-made all the splices and connected receptacles via binding screw in every box on that circuit the nuisance tripping had subsided considerably. However, it was still tripping AFCI a couple times per week. I then replaced the AFCI breaker in panel and it has been holding to this day.
Question: Are there any proposals considered to dis-allow stab-in's when connected to AFCI protected cct?
Thanks in advance for any info on this topic.
Kevin
Question: Are there any proposals considered to dis-allow stab-in's when connected to AFCI protected cct?
Thanks in advance for any info on this topic.
Kevin