stacked meter/disconnects

Status
Not open for further replies.
Re: stacked meter/disconnects

Jim W in Tampa said:
Am i correct in saying i can not have 10 meter disconnects ports without a main breaker

There is no requirement to have a main breaker, only a main disconnect.
 
My problem is the engineer (maybe loco) did not include any disconnect to kill the power to the 10 units short of turning 10 breakers off at meter center.I was looking for reinforcement before i look like a fool in calling him down.Far too often there is an exception that we all miss.Other inputs are welcome.Just what does a 1,000 amp disc cost ?
 