Stadium lighting

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Stadium and sport lighting load is very high, can we use greater than 20A breaker or three-pole breakers greater (> than 20A)
to serve lighting load and still comply with NEC?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Yes. That’s typical. The sports lighting will usually have fuses for each fixture in the driver enclosure.


Sent from my iPhone using Tapatalk
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Stadium lights are typically 'mogul base', your max circuit
size is 50 amp see 410.62(C)(2) and 210.23(C), if the light boxes are cord connected they might come with a UL listing for the whole assembly.
 

bajuiyet

Member
Location
NGN
Occupation
Engineer
Yes. You can use breakers greater than 20A in as much as it is not greater than 50A. 50A is the maximum circuit breaker that can be used
 