I am currently working on a hotel that has 1-hr walls between all rooms with staggered studs for sound purposes.
I have 4" sq. boxes for all the data drops and some receptacles.
I have Allied fiberglass boxes for the majority of outlet/switch boxes.
The fire marshall has accepted my documentation that putty pads are not needed for the Allied boxes installed as close as 3" in the same stud cavity on opposite sides of the wall.
The fire marshall has not accepted my documentation from the IBC for metal boxes installed on opposite sides of the wall.
Her interpretation is that the wall is one stud cavity.
She will not accept the IBC, only Life Safety.:roll:
The IBC clearly allows my installation as long as boxes are not directly back to back.
Does anyone have experience with this?
View attachment 4803
I have 4" sq. boxes for all the data drops and some receptacles.
I have Allied fiberglass boxes for the majority of outlet/switch boxes.
The fire marshall has accepted my documentation that putty pads are not needed for the Allied boxes installed as close as 3" in the same stud cavity on opposite sides of the wall.
The fire marshall has not accepted my documentation from the IBC for metal boxes installed on opposite sides of the wall.
Her interpretation is that the wall is one stud cavity.
She will not accept the IBC, only Life Safety.:roll:
The IBC clearly allows my installation as long as boxes are not directly back to back.
Does anyone have experience with this?
View attachment 4803