This question has come up frequently in design.
How do you ckt fixtures and their location when served by a MWBC?
ie: 3phase,120/208V,using 120v lighting loads protected with single pole breakers,,,,,The Designer often asks or the Client often dictates " circuit grouping or circuit staggering witin an area." The argument for grouping fixtures by one circuit in an area would be>>> if that circuit were interupted for what ever reason then this would naturally create a dark spot and force plant maintenance to act on this. On the other hand if mutiple circuits were used in an area and one of those circuits were interupted the loss of light would be reduced only partially and maintenace could fix at a more convenient time.I always chose the later when client spec gave me the option,basically for possible safety and egress issues.
Now with the advent of NEC 2008,,,,,210.4 requiring that all ungrounded conductors of a MWBC be simultaneously disconnected at the same time then the argument of the two scenarios above becomes mute but brings to mind other scenarios/questions.
If any of the 3 phases in the 120/208 MWBC were to interupt then all 3 phases are lost and a much greater area is in darkness.Does this change lighting design thinking? #1,,, a second MWBC might feed this area as well,#2,,, more emergency fixtures be used,#3,,,additional MWBC in the same area would reduce lighting loads per circuit,#4,,, to use circuit ampacities to their max now has to be rethought,#5 more lightly loaded circuits may lead to more thought out placement of panelboards,maybe even smaller paneboards and transformers.I guess one could go on and on with these "what if's"
I'm not complaining here on this issue or saying it should not be this way but only saying change breeds more changes be it good or bad. Its a pretty good impact to the thinking. I'm sure cost studies will be done by engineering companies to fine the best or thought to be best solutions in design changes.
Do you as the man with the tools see as many impacts on the construction phase with such a small change in phylosophy as seems to be looming in the future of design.
I personally like the thought processes getting shaken up from time to time to keep the boredom down,LOL.
dick
How do you ckt fixtures and their location when served by a MWBC?
ie: 3phase,120/208V,using 120v lighting loads protected with single pole breakers,,,,,The Designer often asks or the Client often dictates " circuit grouping or circuit staggering witin an area." The argument for grouping fixtures by one circuit in an area would be>>> if that circuit were interupted for what ever reason then this would naturally create a dark spot and force plant maintenance to act on this. On the other hand if mutiple circuits were used in an area and one of those circuits were interupted the loss of light would be reduced only partially and maintenace could fix at a more convenient time.I always chose the later when client spec gave me the option,basically for possible safety and egress issues.
Now with the advent of NEC 2008,,,,,210.4 requiring that all ungrounded conductors of a MWBC be simultaneously disconnected at the same time then the argument of the two scenarios above becomes mute but brings to mind other scenarios/questions.
If any of the 3 phases in the 120/208 MWBC were to interupt then all 3 phases are lost and a much greater area is in darkness.Does this change lighting design thinking? #1,,, a second MWBC might feed this area as well,#2,,, more emergency fixtures be used,#3,,,additional MWBC in the same area would reduce lighting loads per circuit,#4,,, to use circuit ampacities to their max now has to be rethought,#5 more lightly loaded circuits may lead to more thought out placement of panelboards,maybe even smaller paneboards and transformers.I guess one could go on and on with these "what if's"
I'm not complaining here on this issue or saying it should not be this way but only saying change breeds more changes be it good or bad. Its a pretty good impact to the thinking. I'm sure cost studies will be done by engineering companies to fine the best or thought to be best solutions in design changes.
Do you as the man with the tools see as many impacts on the construction phase with such a small change in phylosophy as seems to be looming in the future of design.
I personally like the thought processes getting shaken up from time to time to keep the boredom down,LOL.
dick