stair question

Status
Not open for further replies.

alpha_03

Member
Howdy all this is my first time here!

I was wondering - Our instructor states that the NEC makes mention to the requirements for the use of a 3-way with consideration to stairs. Now I do realize that 6 steps or more requires a 3-way, however, his question related to finding the specfic location in the code book- and even he couldn't do this- any Ideas?

TY in advance. :)
 

bill addiss

Senior Member
Re: stair question

Alpha,

The code doesn't mention 3-ways specifically, only requiring that there is a wall switch at each level to control the lighting outlet(s) that are installed there.

Look at 210.70(A)(2)(c) for the specific language

Bill
 

alpha_03

Member
Re: stair question

howdy Bill and thanks for your reply. so is that to say that 3-ways are not required for stairs or other areas in accordence with the nec rules and regs? as it apears the code does not require this, rather, it's more a convienance (obviously one would prefer and should install 3-ways for 6-stairs or more, or for multiple entries and exits).
 

bill addiss

Senior Member
Re: stair question

so is that to say that 3-ways are not required for stairs or other areas in accordence with the nec rules and regs?
alpha,

It seems that separate fixtures with switches on each level would also be compliant, although probably not practical.

Bill
 

alpha_03

Member
Re: stair question

thanks guys- i am now armed for class, my instructor swears that it list this in the nec 2002 code book (in a place that one would not normally look) but he must be mistaken. any way the point is not about right or wrong, rather, the knowledge gained from others - thank you.

[ November 08, 2003, 12:06 AM: Message edited by: alpha_03 ]
 

rickg

Member
Location
Rhode Island
Re: stair question

alpha_03
The IRC & the CABO codes require that stairway illumination be controlled from each level. It makes no mention of the # of stairs, just each level. So if you position a switch that is accessible from both levels you would only need one switch. Sometimes this is the case where there only one or two stairs between levels, such as from a garage to the dwelling.
 