I'm wiring a new addition. There is a large open living room area with an open stairway to a balcony and second floor bedrooms. The first riser of the stairway starts right next to a double pocket door going into a room. There is no place to install the switch for the stairway light that seems code legal. The pocket door will hit any box installed in the wall for the first 30". I currently have the box installed just past the pocket door which places it at about the fifth riser i.e. you have to walk up a few steps to reach the switch. Going back away from the stairs, the opposing pocket door takes up all the wall space and then there is a large post past that. Is my box at the fifth riser legal?
The client wants to put the switch inside the pocket door room since there is already a 3 gang box there. I don't think this is code legal nor convenient (when the doors are closed). Agree?
I know I can use Wiremold, but I looking for other solutions first.
210.70 (A)(2)(c) Where one or more lighting outlet(s) are installed
for interior stairways, there shall be a wall switch at each
floor level, and landing level that includes an entryway, to
control the lighting outlet(s) where the stairway between
floor levels has six risers or more.
The client wants to put the switch inside the pocket door room since there is already a 3 gang box there. I don't think this is code legal nor convenient (when the doors are closed). Agree?
I know I can use Wiremold, but I looking for other solutions first.
210.70 (A)(2)(c) Where one or more lighting outlet(s) are installed
for interior stairways, there shall be a wall switch at each
floor level, and landing level that includes an entryway, to
control the lighting outlet(s) where the stairway between
floor levels has six risers or more.