- Northeast, PA
- Occupation
- Electrical Design
Customer sent a cut sheet of an emergency generator they own and want to use to back up a new restaurant they are constructing. My question is regarding the actual capacity available from the generator. There is a circuit breaker installed directly on the unit rated at 800A. I know there are several factors to consider like motor in rush, starting load etc, etc that factor into this generator. Ultimately I am wondering why do they list on the cut asheet the ampacity based on KVA of the unit when the breaker is clearly set based on KW. 120/208V 3 phase. I would calculate this generator to be capable of 694 loaded to 100%. If KVA can be used we have much more capacity.