Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
I am having brain fog today. Must be the weather around here today.
If a building by calculation of the loads requires a 3000kVA transfomer for the service would it be a 3000kVA generator to back up the building properly?
By standards .8pf is used for stand-by gen sets which makes that 3000kVA generator 2400kW.
Math tells me
3000kVA = 3605A
2400kW = 2884A
In stand-by gen sets should kW size equal the utility transformer kVA.
I am missing something simple here so I hate asking but I can not wrap my head around this today. Likely the 12hours I worked yesterday to get a project done for a client.
Thanks for looking