Greetings,
I've got a stand-by diesel generator feeding a small pump station. I'm trying to evaluate the system from system protection perspective. The caveat here is there is no neutral brought to the MCC, since there are not single phase loads.
I've got two scenarios:
1. For Y-connected load, for phase to neutral fault, I'm assuming all three phases will be affected, as there is no neutral wire to carry unbalanced current. In this scenario, genset breaker will pop on the overcurrent and/or phase unbalance.
2. For Y or Delta connected load, for ground fault, the system will be largely unaffected. My reasoning is that there is no system ground in the system and no neutral wire available for ground fault return path, thus there is no ground return path to the system source.
Please see attached my diagram. Please share your thoughts and good technical reference if you can recommend one.
Thanks,
EE
I've got a stand-by diesel generator feeding a small pump station. I'm trying to evaluate the system from system protection perspective. The caveat here is there is no neutral brought to the MCC, since there are not single phase loads.
I've got two scenarios:
1. For Y-connected load, for phase to neutral fault, I'm assuming all three phases will be affected, as there is no neutral wire to carry unbalanced current. In this scenario, genset breaker will pop on the overcurrent and/or phase unbalance.
2. For Y or Delta connected load, for ground fault, the system will be largely unaffected. My reasoning is that there is no system ground in the system and no neutral wire available for ground fault return path, thus there is no ground return path to the system source.
Please see attached my diagram. Please share your thoughts and good technical reference if you can recommend one.
Thanks,
EE