wireguy8169
Senior Member
- Location
- Southern Maine
Hello,
I am using the text "Electrical Systems" for an NEC course (I used this book back in my apprenticship too), anyhow while doing the standard load calculation specifically the part for fixed appliances the text does not deduct the portion of the load for the water heater (240V is specified not a on demand or anything like that). Even on the website that the text gives a video tutorial it shows the same calculation and again does not deduct that portion of the load before doing the demand for the neutral part of the load. Here is the example
Dishwaser =1650 Disposer=950 Compactor=700 Water Heater=7500 Attic Fan=1400 for a total of 12,200VA
there are four or more appliances so I am permitted to apply the demand factor
So I use the demand 12200 x .75 = 9150VA (this is the general load) Phase
I go on to figure the neutral load, I re do the calculation deducting the water heater (this still leaves me four or more so I am permtitted to apply the demand factor)
So now I have (1650 +950+700+1400=4700VA )
Apply the demand factor 4700 x .75 = 3525VA (for my neutral load)
This is the answer I get
Phase = 9150 Neutral = 3525
The text gives an answer of phase 9150 and neutral 9150 (I do realize you do not have to apply a demand factor at all but this is what the chapter is covering)
Thanks
I am using the text "Electrical Systems" for an NEC course (I used this book back in my apprenticship too), anyhow while doing the standard load calculation specifically the part for fixed appliances the text does not deduct the portion of the load for the water heater (240V is specified not a on demand or anything like that). Even on the website that the text gives a video tutorial it shows the same calculation and again does not deduct that portion of the load before doing the demand for the neutral part of the load. Here is the example
Dishwaser =1650 Disposer=950 Compactor=700 Water Heater=7500 Attic Fan=1400 for a total of 12,200VA
there are four or more appliances so I am permitted to apply the demand factor
So I use the demand 12200 x .75 = 9150VA (this is the general load) Phase
I go on to figure the neutral load, I re do the calculation deducting the water heater (this still leaves me four or more so I am permtitted to apply the demand factor)
So now I have (1650 +950+700+1400=4700VA )
Apply the demand factor 4700 x .75 = 3525VA (for my neutral load)
This is the answer I get
Phase = 9150 Neutral = 3525
The text gives an answer of phase 9150 and neutral 9150 (I do realize you do not have to apply a demand factor at all but this is what the chapter is covering)
Thanks