Standard load calc

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi
is standard load calc a good methods calc for sizing the service of a 11- unit apartment bldg
the total ltg. /small appliance load is 8000 VA
no air condition
no laundry


1st 3000 @ 100%. 3000VA
120000 -3000 @ 35%. 40950 VA

totoal connected load. 43950 vA
or. 183 amp
 
Hi
is standard load calc a good methods calc for sizing the service of a 11- unit apartment bldg
the total ltg. /small appliance load is 8000 VA
no air condition
no laundry


1st 3000 @ 100%. 3000VA
120000 -3000 @ 35%. 40950 VA

totoal connected load. 43950 vA
or. 183 amp
You got 183 amps for a service for an 11 apartment building..????:huh:
 