Re: Standard Load Calc.
You are talking about the demand factors for the lighting loads, per Table 220.11. You start with the 3 VA per square foot. There are only two other things that you can add to this lighting load, before applying the demand factor. They are the two small appliance circuits (3000 VA total) and one laundry circuit (1500 VA). You apply the demand factor (100% of the first 3000 VA, 35% of the next 170,000 VA, and 25% of the rest). Then, and only then, you add the motors (dishwasher, trash compactor, garbage disposal) and all the other loads. These three specific motor loads are not included in the loads to which Table 220.11 applies.