Question, sometime when we size OCPD, we need to use one size down. For example, I have a switchboard contain motor and other load.
480V 3P switchboard with all 3p equipment.
400HP motor 1 with VFD: 477A FLA
400HP motor 2 with VFD: 477A FLA
250HP motor 3 with VFD: 302A FLA
60HP motor 4: 77A FLA
other load: 640A
Main OCPD= 477*1.75=834.75 next size up 1000.
1000+477+302+77+640= 2496A, next size down 2000A.
So main OCPD is 2000A.
Question, will it down size too much? i mean it is about 496A different. it more than the different you size up, you only size up 165.25A.
The big standard OCPD have big jump. 2000, 2500, 3000, 4000. will you feel comfortable when you using next size up or down for the big OCPD?