brycenesbitt
- United States
Monday August 18 2025 10am EST is the 2025 Standards Council Meeting. Agenda is at
http://www.nfpa.org/sc2025
You have to appear in 15 minutes in advance virtually or in person to register.
There's an item there that started with Public Input No. 1440 by a member of this very forum. That PI was later releveled to have had a different purpose as a challenge to another rule (and variously as a "joke"). Yet:
This change has a similar impact to 210.8(F) in creating significant angst among those working in the space. The risk data is just not there to justify an action that will create secondary risks. It's a solution worse than the (theoretical) problem. Diligent searches by various parties including SAE and UL have shown there is no problem to solve: the existing system is working fine. And my view is adding SPGFCI is another bad solution that still misses the safety point.
Anyway here's the core appeal document, as supported by Honda, Rivian, Chargepoint, Electric Drive Transport Association and more:
National Fire Protection Association
1 Batterymarch Park
Quincy, Massachusetts U.S. 02169-7471
July 11, 2025
Attention: Mr. Dwayne E. Sloan
Secretary, NFPA Standards Council
Regarding: 2026 National Electrical Code Making Process
National Electrical Code Making Panel 12
Matters of 2025 Certified Amendment Motions affecting NEC 625.54
CAM 70-58/70-77/70-147/70-151/70-178
CAM 70-134/70-182
CAM 70-135/70-142/70-145/70-179
Dear Mr. Sloan:
We, as members of the auto industry, appreciate NFPA's dedication to improving Article 625 of National Electrical Code, "Electric Vehicle Power Transfer System." As of 2024, about 4 million electric vehicles are on road in the United States according to an Experian Automotive report. It is important for us to offer safe and reliable electric vehicle charging environment to users of those vehicles in a code-compliant and affordable manner.
As we approach the end of the revision cycle of 2026 Edition of National Electrical Code, we are concerned that elements of the current Drafts text are incompatible with ANSI/UL EVSE standards resulting in customers being unable to charge their vehicles. We see key issues that were not addressed in the Drafts and were not solved in the 2025 Technical Meeting of the NFPA Conference and Expo held in Las Vegas, NV on June 19-20, 2025.
The grounds for this Appeal are structured under three categories:
SAE International Standards Chair for
Electric Vehicle Conductive Power Transfer for the Motor Vehicle Council
and the Truck and Bus Council
139 The Green
Newark, Delaware 19716 USA
The lack of technical substantiation was evident from the First Draft stage, and the requirements were significantly expanded yet again in the Second Draft without providing experts the opportunity to provide input. Even the original submitter of this public input later submitted Public Comment No. 275 asking the committee to reverse their action based on the lack of substantiation. Other public comments correctly identified a lack of technical substantiation.
1. Unclear and Ambiguous Effective Dates:
Documented empirical evaluations have proven that the proposed requirements are not merely impractical, but they conflict with prevailing standards and are impossible to implement:
1 Batterymarch Park
July 11, 2025
CAM 70-134/70-182
Dear Mr. Sloan:
- Non-compliance with Regulations Governing the Development of NFPA Standards
- Inconsistencies under NEC Style Manual: Clarity and Usability
- Nonadherence to NFPA’s Guide for the Participants in the NFPA Standards Development Process
1. NAME, AFFILIATION, AND ADDRESS OF THE APPELLANT
Dr. Rodney McGee PESAE International Standards Chair for
139 The Green
2. STATEMENT IDENTIFYING THE PARTICULAR ACTION TO WHICH THE APPEAL RELATES
This appeal relates to the failed Certified Amending Motion CAMs, 70-58/70-77/70-147/70-151/70-178, concerning NFPA 70 Article 625.54, which were rejected at the 2025 NFPA Annual Technical Meeting held in Las Vegas, NV on June 19-20, 2025.3. ARGUMENT SETTING FORTH THE GROUNDS FOR THE APPEAL
The development and approval of the proposed 2026 NEC Section 625.54 text violated multiple provisions of NFPA's governing documents, resulting in technically unsound and unusable requirements that will harm public safety and the electric vehicle infrastructure.A. Compliance to Regulations Governing the Development of NFPA Standards
1. Section 4.3.4.1(d) and (e) - Lack of Technical Substantiation for Public Input
Public Input No. 1440 expanded the requirements of 625.54 to add GFCI or SPGFCI for outlets without providing any technical substantiation or data to justify this expansion.The lack of technical substantiation was evident from the First Draft stage, and the requirements were significantly expanded yet again in the Second Draft without providing experts the opportunity to provide input. Even the original submitter of this public input later submitted Public Comment No. 275 asking the committee to reverse their action based on the lack of substantiation. Other public comments correctly identified a lack of technical substantiation.
2. Section 4.3.9.2.2 - Inadequate Committee Statement
The Committee Statement on Public Comment No. 1440 failed to provide any technical substantiation or data justifying the expansion of requirements of 625.54.3. Section 4.4.8.2 - Insufficient Technical Rationale in Second Draft
Section 4.4.8.2 provides that committee statements "shall preferably be technical in nature and shall be sufficiently detailed so as to convey the committee's rationale," but the committee statement associated with Second Draft Revision No. 7875:- Provided insufficient technical substantiation or data explaining why the committee ignored technical incompatibilities identified in the ballot.
- Created contradictions with the published text, including conflation of GFCI and SPGFCI requirements.
- Did not clarify the applicability of effective dates as they pertain to GFCI versus SPGFCI and related voltage levels.
Section 1, Purpose - Included Language does not Achieve Clarity and Usability
The Style Manual requires technical committees to produce documents "as clear, useable, and unambiguous as possible." The current text conflicts with this fundamental purpose in multiple ways:1. Unclear and Ambiguous Effective Dates:
- 625.54(B)(2) states the effective date of January 1, 2029
- The committee statement in the Second Revision, 7875, regarding the exception claims this date applies to all of 625.54(B).
- However, 625.54(B)(1) contains no such effective date language.
- The resulting language introduces confusion about implementation requirements.
- Verified Heavy-Duty Vehicle Failures: Empirical evidence was included in the documentation for the NITMAM CAM 70-54. This data was collected during field testing where it verified failed operation of commercially available electric bus models used by First Student (the largest school bus operator in the US). These vehicles utilize single-phase 208VAC for AC EVSE, and none were able to charge at all from Class A GFCI as required by the 2026 625.54(B)(1).
- Broader Impact: Identical school bus charging components are utilized in other heavy-duty vehicles, this failure pattern extends across not only the heavy-duty vehicle but also all automotive sectors.
- Passenger Vehicle Incompatibility: Multiple OEMs have produced test data which shows significant performance variability for passenger cars and pickup trucks. These data support findings that many cannot operate at all, while others trip unpredictably.
- Bidirectional Charging: Systems falling under 625.54(B)(1) would require GFCI protection, yet no GFCI or SPGFCI products exist that are compatible with bidirectional charging.
- Exception 2 lacks GFCI-specific language for a bidirectional use case and applies only to SPGFCI under 625.54(B)(2).
- The proposed language is unusable for residential or commercial 120/240V and 120/208V installations because EVSE under Section 625.54(B)(1) are required to use GFCI, not SPGFCI.
- Importantly, this contradicts CMP-12's stated intent regarding the January 2029 implementation timeline for all EVSE under 625.54(B). The committee statement is as follows: "625.54(B): The January 1, 2029 date allows the industry time to develop the technology for power export and GFCI protection."