hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
See attached sketch. I have 25kw, 240/120V single phase standby generator for cell site.
The 240V, 2 poles ATS has two breakers in it. One for cam lock 200A breaker and the other for the generator 125A breaker. The ATS feeds the downstream 200A panelboard.
When the ATS flips to generator it would be powering both the cam lock as well as 200A panelboard having demand load of 93A at present.
When the ATS flips to the utility the generator can still power the camlock.
The generator is not separately derived and normal utility power source is 240/120V single phase.
Following question:
1. Does the NEC 2014 say anything about cam locks anywhere?
2. Does the NEC 2014 say anything about cam lock ratings?
3. When ATS flips to generator, the 25kW full load amps is 104A. Panelboard demand amps is 93A. Is not the generator too small with comlock? Is their section in regards to how to size the standby generator?
4. When ATS flip to utility the generator FLA is 104A however downstream breaker provided is 200A is that ok?
The 240V, 2 poles ATS has two breakers in it. One for cam lock 200A breaker and the other for the generator 125A breaker. The ATS feeds the downstream 200A panelboard.
When the ATS flips to generator it would be powering both the cam lock as well as 200A panelboard having demand load of 93A at present.
When the ATS flips to the utility the generator can still power the camlock.
The generator is not separately derived and normal utility power source is 240/120V single phase.
Following question:
1. Does the NEC 2014 say anything about cam locks anywhere?
2. Does the NEC 2014 say anything about cam lock ratings?
3. When ATS flips to generator, the 25kW full load amps is 104A. Panelboard demand amps is 93A. Is not the generator too small with comlock? Is their section in regards to how to size the standby generator?
4. When ATS flip to utility the generator FLA is 104A however downstream breaker provided is 200A is that ok?