Hello:
New to this forum and thought I could get some input on a Standby Generator problem.
I have an all electric house and recently sought quotes on a standby generator. I immediately got pushback due to the 20kw resistance heat that is part of my geothermal heating system. I propose reducing it to 10kw but that still didn't excite anyone.
After looking at the problem for awhile I came up with a possible solution. The attached sketch will better describe my idea.
1st I need to isolate the 10kw from the "Main Housel Load Center" (MHLC) and then group together then mandatory circuits that need to fed whether the the "10 kw Resistance Heat"(10kWRH)is on or the MHLC. These would be 2 refrigerators, a freezer and garage door openers. This would be a subpanel fed from the MHLC and the 10KWRH with a manual transfer switch #2 controlling the source.
Starting at the beginning of the circuit there would be a conventional standby generator installation, Utility Power, Generator, and ATS. From the ATS power would go through a 200 amp Safety Switch #1 that would direct the source to the MHLC position "A" or the 10KWRH position "B". in parallel with that switch #2 would be in the same "A" or "B" position which would direct power to the Mandatory Loads based on the source selected by switch #1.
I don't know if here are any smaller alternatives to the 200 amp safety switch it's 37" x 11"x 6". "massive"
I still don't know if the 20kw generator will handle the rest of the house but if not that will just add a conventional generator panel to handle the necessary load items along with the mandatory load items.
The main problem is getting anyone to talk about if. The contractors see that 20kw/100amp breaker in the panel and the law says if you hook up to the panel the generator has to handle the load. I'm hoping this will satisfy the requiremnent.
there doesn't appear to be and potential feedback or dual source issues. The safety switch is supposed to prevent any arc issues during switching.
Thanks

New to this forum and thought I could get some input on a Standby Generator problem.
I have an all electric house and recently sought quotes on a standby generator. I immediately got pushback due to the 20kw resistance heat that is part of my geothermal heating system. I propose reducing it to 10kw but that still didn't excite anyone.
After looking at the problem for awhile I came up with a possible solution. The attached sketch will better describe my idea.
1st I need to isolate the 10kw from the "Main Housel Load Center" (MHLC) and then group together then mandatory circuits that need to fed whether the the "10 kw Resistance Heat"(10kWRH)is on or the MHLC. These would be 2 refrigerators, a freezer and garage door openers. This would be a subpanel fed from the MHLC and the 10KWRH with a manual transfer switch #2 controlling the source.
Starting at the beginning of the circuit there would be a conventional standby generator installation, Utility Power, Generator, and ATS. From the ATS power would go through a 200 amp Safety Switch #1 that would direct the source to the MHLC position "A" or the 10KWRH position "B". in parallel with that switch #2 would be in the same "A" or "B" position which would direct power to the Mandatory Loads based on the source selected by switch #1.
I don't know if here are any smaller alternatives to the 200 amp safety switch it's 37" x 11"x 6". "massive"
I still don't know if the 20kw generator will handle the rest of the house but if not that will just add a conventional generator panel to handle the necessary load items along with the mandatory load items.
The main problem is getting anyone to talk about if. The contractors see that 20kw/100amp breaker in the panel and the law says if you hook up to the panel the generator has to handle the load. I'm hoping this will satisfy the requiremnent.
there doesn't appear to be and potential feedback or dual source issues. The safety switch is supposed to prevent any arc issues during switching.
Thanks