STANDBY GENERATOR HIGH LEG

Status
Not open for further replies.

paradise

Member
Location
florida
I have installed commercial generators for years but never installed one on a high leg service. Recently customer request a standby generator for a commercial office that has 3 phase 120/240 delta high leg. What is required when specifying the generator hardware? To the best of my knowledge there is no such thing as a commercially available high leg generator?
 
Keep in mind that a very common form of generator has a '12 lead' alternator. This has 6 separate 120-150V coils which can be connected in various ways to get pretty much any of the standard utilization connections, including 240/120V high leg delta.

The supplier may need to do some internal connecting, but this should not be a big problem.

-Jon
 
SUPPLIER RESPONSE

SUPPLIER RESPONSE

Thanks for the tips. I talked to the supplier's (distributors) sales engineer and his said that they don't have a high leg generator. I spec'd a 120/240V 3? 4W unit.
He said that this will simply connect like any delta 3? power source NO HIGH LEG. That is a little surprising considering that I have 208 volt loads using hi leg. Maybe I need to talk to mfg engineer prior to delivery. Maybe he knows more about alternator than salesman and can pre-configure my unit at factory for a minimum of field hassle.
 
Thanks for the tips. I talked to the supplier's (distributors) sales engineer and his said that they don't have a high leg generator. I spec'd a 120/240V 3? 4W unit.
He said that this will simply connect like any delta 3? power source NO HIGH LEG. That is a little surprising considering that I have 208 volt loads using hi leg. Maybe I need to talk to mfg engineer prior to delivery. Maybe he knows more about alternator than salesman and can pre-configure my unit at factory for a minimum of field hassle.

Two big problems with his approach:
1. You will get 208 volts for your existing 240 loads.
2. Any 120/240 three wire MWBCs will change to having the neutral counted as a CCC. This may or may not cause a derating problem.
One more concern: Using your existing high leg to neutral for 208 volt loads rather than for three wire 240V three phase loads is not a good idea and causes unusual transformer loading that is often not calculated properly, especially in an open delta.
 