Standby generator residential

Status
Not open for further replies.

Peter Furrow

We’re not born humble, we’re born to be humbled
Location
Cape canaveral Fl
Occupation
Electrical contractor
As you know optional standby generator systems is taken out of article 702.
I have to run 100 amp feeders from the transfer switch to the generator. Some electrical contractors have told me that the 83% rule does not apply.
I would like to run # 2 AL 75° column 90 amp rated.
Or do I have to run #1 Al 75° column 100 amp rated?


Sent from my iPhone using Tapatalk
 
Possibly an AHJ decision.
It was discussed here recently:

but, the issue was brought before State AHJs here and they will not allow the 83% rule on generator feeders.
 