Ok guys I've got a strange one. We have a remote pumping facility with a generator backup. For years this unit operated with no problems supplying power for two three phase 40hp vfd and control panel. Lately the generator will start hunting when under load from either vfd not alot of rpm difference maybe 50 rpm or so. The control panel is single phase with a small battery backup. When we start one of the pumps the controls start acting strangely the battery backup still shows 117 volts but it causes the PLC to act erratically there has been control wiring changes over the years. We have had the local CAT generator people out who brought out their engineers and could not find any problem other than a leading pf on utility and a lagging pf on generator when the vfd is running. Keep in mind that it worked fine for the last 10+ years. And one of the vfd's is new. The generator will get a vars fault if you try to run both pumps at the same time, something you were able to do in the past. Any ideas?
.
.