I HAVE INSTALLED NUMEROUS STANDBY GENERATORS. I NOW HAVE AN INSPECTOR THAT IS TURNING ME DOWN FOR THIS:
ON A 200 AMP METER BASE, INSTALL A SERVICE ENTRY RATED, NEMA3 AUTO. TRANSFER SWITCH NEXT TO METER BASE. WIRE FROM LOAD SIDE OF METER BASE TO TRANSFER SWITCH, THEN TO 200 AMP BREAKER PANEL.
INSPECTOR NOW SAYS:
SINCE THE TRANSFER SWITCH IS NOW CONSIDERED THE FIRST MEANS OF DISCONNECT THE BREAKER PANEL IS A SUB PANEL. 1.THEREFORE YOU MUST SEPARATE ALL YOUR GROUNDS AND NEUTRALS IN BP, 250.24.A5 2. THE GROUNDING ELECTRODE CONDUCTORS MUST TERMINATE IN THE FIRST MEANS OF DISCONNECT. 250.24.A1 3. GROUNDING ELECTRODE CONDUCTORS CANNOT BE SPLICED. 250.64C 4. NEED TO BOND THE GAS LINE 250.104B 5. INTERSYSTEM BONDING TERMINATION REQUIRED 250.94
THERFORE I HAVE TO INSTALL NEW GROUNDING ROS AT PANEL...AS WELL AS THE OTHER LISTED ITEMS. IS THIS INSPECTOR RIGHT?
ON A 200 AMP METER BASE, INSTALL A SERVICE ENTRY RATED, NEMA3 AUTO. TRANSFER SWITCH NEXT TO METER BASE. WIRE FROM LOAD SIDE OF METER BASE TO TRANSFER SWITCH, THEN TO 200 AMP BREAKER PANEL.
INSPECTOR NOW SAYS:
SINCE THE TRANSFER SWITCH IS NOW CONSIDERED THE FIRST MEANS OF DISCONNECT THE BREAKER PANEL IS A SUB PANEL. 1.THEREFORE YOU MUST SEPARATE ALL YOUR GROUNDS AND NEUTRALS IN BP, 250.24.A5 2. THE GROUNDING ELECTRODE CONDUCTORS MUST TERMINATE IN THE FIRST MEANS OF DISCONNECT. 250.24.A1 3. GROUNDING ELECTRODE CONDUCTORS CANNOT BE SPLICED. 250.64C 4. NEED TO BOND THE GAS LINE 250.104B 5. INTERSYSTEM BONDING TERMINATION REQUIRED 250.94
THERFORE I HAVE TO INSTALL NEW GROUNDING ROS AT PANEL...AS WELL AS THE OTHER LISTED ITEMS. IS THIS INSPECTOR RIGHT?