Yes here it is, another one of my meaningless Polls... Actually they mean something to me, and might mean something to someone out there besides me
M. D. said:In Massachusetts we have to use plastic for smaller cables
Thank you, Charlie.cpal said:334.30 Revise 334.30 as follows [(A), (B), and (C) unchanged from NEW}:
334.30 Securing and Supporting. Nonmetallic-sheathed cable shall be secured by staples, cable
ties, straps, or similar fittings so designed and installed as to not damage the cable. Where staples are used for cable sizes smaller than 8 AWG conductors, they shall be of the insulated type, or listed noninsulated staples driven by staple guns shall be permitted. Cable shall be secured in place at intervals not exceeding 1`.4 m (4 ? ft) and within 300 mm (12 inc.) from every cabinet, box, or fitting. For other than within 300 mm (12 inc0 of a cable termination at a cabinet, box, or fitting, cables passing through successive holes in adjacent framing members no more than 600 mm (24 in.) apart shall be considered to be secured.
Charlie
izak said:but ill try to be alittle more conservative with that button in the future...
![]()
Lady Engineer said:that's ok sweetie, it's breaks the manotony!![]()
dlhoule said:Was that intentional or otherwise. manotony as opposed to monotony?:wink: