Star Delta Motor....No Timer?

Status
Not open for further replies.
I am currently building a new control panel to replace the outdated one for a large two speed cooling fan. The fan has a Low Speed Contactor, a High Speed Contactor, and a Star Contactor operating in conjuction with the high speed contactor. The contactors are wired as you would typically find for Star/Delta High Speed. However, there is currently no timer to disengage the Star Contactor. So...during the entire High Speed operation, both the Star and High Contactor remain engaged. What could the possible reason for this be?
 
It's a 2 speed 1 winding motor. The circuit looks like a wye-delta starting scheme to the untrained eye but it's different. If you look at it in this drawing, they show one contactor as if it is 5 pole, but that doesn't exist, so it's done with two contactors that close together. image004.jpg
 
Status
Not open for further replies.
Top