This is pertaining to cable selection for star-delta starter which is to be connected from a panel. It is understood that we have six terminals from star-delta starter to connect to motor (i.e. two runs of 3-core cables from star-delta starter are to be connected to motor). Should the cable from panel to star-delta starter be greater in size as compared to that from star-delta starter to motor.
A sample calculation is as follows:-
Main Supply Voltage = 400V, 3Phase, 50Hz
Motor Power = 18.5kW [52 hp] (Condenser Pump)
Starting Method = Star Delta
Distance from the panel to starter = 1m
Distance from the starter to motor = 20m
Parameters to be calculated are:-
a. MCCB rating
b. Cable size from main supply panel to starter and from starter to motor
Load current Calculation
Full Load Current = 18.5kW/1.732*400*0.85*0.94 (0.85 = p.f and 0.94 = efficiency)
FLC = 33.42A say 34A
MCCB = 1.5*FLC = 1.5*34A = 51A (choosing next higher rating say 63A)
(whether the MCCB selection is Ok? Or should I go for 2.5 times of FLC.)
Cable size selection
From Panel to starter
MCCB rating =63A
Cable size = 16 sq. mm Aluminium (Cable ampere rating = 62A)
Cable Size from starter to motor
We have 6 cables going from the starter to motor. Each set of cable need to be rated at 58% of the FLC. Therefore
Cable current = 0.58*34 = 19.72A
Cable size = 6 sq. mm Aluminium (Cable ampere rating=43A)
Please check and comment on the calculation
A sample calculation is as follows:-
Main Supply Voltage = 400V, 3Phase, 50Hz
Motor Power = 18.5kW [52 hp] (Condenser Pump)
Starting Method = Star Delta
Distance from the panel to starter = 1m
Distance from the starter to motor = 20m
Parameters to be calculated are:-
a. MCCB rating
b. Cable size from main supply panel to starter and from starter to motor
Load current Calculation
Full Load Current = 18.5kW/1.732*400*0.85*0.94 (0.85 = p.f and 0.94 = efficiency)
FLC = 33.42A say 34A
MCCB = 1.5*FLC = 1.5*34A = 51A (choosing next higher rating say 63A)
(whether the MCCB selection is Ok? Or should I go for 2.5 times of FLC.)
Cable size selection
From Panel to starter
MCCB rating =63A
Cable size = 16 sq. mm Aluminium (Cable ampere rating = 62A)
Cable Size from starter to motor
We have 6 cables going from the starter to motor. Each set of cable need to be rated at 58% of the FLC. Therefore
Cable current = 0.58*34 = 19.72A
Cable size = 6 sq. mm Aluminium (Cable ampere rating=43A)
Please check and comment on the calculation