Starter Protection

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
This data sheet accompanied a A-B 509-BOD NEMA Starter.
You will not the reference to the SCGF protective device for this starter is for a 30 amp Class R Fuse or 50 amp Class J.
There is no breaker listed.

Does this indicate that the starter MUST have fuse protection and not C/B protection ?

http://raise.rockwellautomation.com...cuit.asp?CID=268AE938B33D483286BB88226E38BB2D


Short Circuit Ratings
Operational RatingDual Element Time Delay FusesNon-Time Delay FusesCircuit BreakersRating ReferenceFile Ref: ULFile Ref: CSAComments
SCCR [kA]Max Fuse Size[A]Fuse ClassSCCR [kA]Max Fuse Size[A]Fuse ClassCB TypeCatalog NumberSCCR [kA]SCCR [kA]SCCR [kA]SCCR [kA]SCCR [kA]
600V600V240V480V480Y/277V600V600Y/347V
? 10030R? ? ?

? ? ? ? ? Label with ProductE3125LR1234
? 10050J? ? ?

? ? ?
 