starting gen

Status
Not open for further replies.
I work at a plant that uses a generator for backup power in a failure. The electricity comming into our plant is 460 volts at 3000amps . According to the 70e safety code is there any ppe needed for testing the switchgear or resetting them in a failure? Am I limited to a certain level work like IR testing?
 

WorkSafe

Senior Member
Location
Moore, OK
Okay, I'll take a stab at it. I am not an electrician, however.

If these switches are in a approved enclosure, which prevents the employee from coming in contact with energized equipment then no PPE is required, BUT, a arc flash analysis should be conducted on this equipment to determine other requirements (70E 130.3)

Hope this helps.
 

nolabama

Senior Member
Location
new orleans la
Obviously you will need to determine the failure. You should/would encounter situations that may need PPE while doing this. If you open that switchgear cabinet with it on you will need PPE.
 