When I was in a Delaware hotel I noticed that Exit signs were mounted near the ceiling and floor. In Massachusetts that is not the case.

That got me thinking about other differences and amendments between the states.

Any feedback is welcome.

In Massachusetts 334.30 was amended to state ?Where the cable is run diagonally behind strapping of a nominal 19 mm (3/4-in) thickness it shall be considered supported, secured, and in compliance with 334.17 where it is not pulled taut.?

Personally I think that this type of installation is a mess, no pride in work.


In Massachusetts a new section 368.14 in part II of article 368 was added
?368.14(A) During Construction. Indoor busways shall be protected from moisture during storage as well as during or after installation..?

Temporary stringers with incandescent lamps installed in transformers and switch gear prior to installation and during storage works well with moisture issues. Not sure if that would work with busways.
 
If you are asking what differences/amendments there are, in VA we follow the 2005 NEC with these amendments:

CHAPTER 27
ELECTRICAL
Change Section 2701.1 of the IBC to read:
2701.1 Scope. This chapter governs the electrical components, equipment and systems used in buildings and structures covered by this code. Electrical components, equipment and systems shall be designed and constructed in accordance with this code and NFPA 70. Any reference in this code to the ICC Electrical Code shall be considered to be references to NFPA 70.
Add Section 2701.1.1 to the IBC to read:
2701.1.1 Changes to NFPA 70. The following change shall be made to NFPA 70:
1. Change Sections 334.10(2) and 334.10(3) of NFPA 70 to read:
(2) Multifamily dwellings not exceeding four floors above grade and multifamily dwellings of any height permitted to be of Types III, IV and V construction except in any case as prohibited in 334.12.
(3) Other structures not exceeding four floors above grade and other structures of any height permitted to be of Types III, IV and V construction except in any case as prohibited in 334.12. In structures exceeding four floors above grade, cables shall be concealed within walls, floors or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
For the purpose of Items 2 and 3 above, the first floor of a building shall be that floor that has 50 percent or more of the exterior wall surface area level with or above finished grade. One additional level that is the first level and not designed for human habitation and used only for vehicle parking, storage or similar use shall be permitted.
Add Section 2701.1.2 to the IBC to read:
2701.1.2 Temporary connection to dwelling units. The building official shall give permission to energize the electrical service equipment of a one- or two-family dwelling unit when all of the following requirements have been approved:
1. The service wiring and equipment, including the meter socket enclosure, shall be installed and the service wiring terminated.
2. The grounding electrode system shall be installed and terminated.
3. At least one receptacle outlet on a ground fault protected circuit shall be installed and the circuit wiring terminated.
4. Service equipment covers shall be installed.
5. The building roof covering shall be installed.
6. Temporary electrical service equipment shall be suitable for wet locations unless the interior is dry and protected from the weather.
Add Section 2701.1.3 to the IBC to read:
2006 VIRGINIA CONSTRUCTION CODE (Part I of the Virginia Uniform Statewide Building Code) ? Effective May 1, 2008
- 73 -
2701.1.3 Assisted living facility generator requirements. Generators installed to comply with regulations for assisted living facilities licensed by the Virginia Department of Social Services shall be permitted to be optional standby systems.
Change Section 2702.2.17 of the IBC to read:
2702.2.17 Group I-2 and I-3 occupancies. Emergency power shall be provided in accordance with Section 407.8 for Group I-2 occupancies licensed by the Virginia Department of Health as a hospital, nursing or hospice facility. Emergency power shall be provided for doors in Group I-3 occupancies in accordance with Section 408.4.2.
 
In Massachusetts 334.30 was amended to state ?Where the cable is run diagonally behind strapping of a nominal 19 mm (3/4-in) thickness it shall be considered supported, secured, and in compliance with 334.17 where it is not pulled taut.?

Personally I think that this type of installation is a mess, no pride in work.

That works out OK as the MEC is supposedly a safety code not a neatness and pride standard. :cool:

You are never prevented from exceeding the NEC.:)
 