Im in a situation where I am being asked to state the code section that does not allow the Eposed use of THHN wiring. The previous electrician or handyman ran 277v THHN to a low voltage 24v transformer. This is clearly going to have to get ripped out but I am actually having a tough time providing the code section.
Here is what I have.
300.3(A) Single Conductors - Single conductors specified in Table 310.104(A) shall only be installed where part of a recognized wiring method of Chapter 3.