Re: Static ground testing
Originally posted by bnewport:
Is this tester the proper way to test this type of ground, or is this strictly for testing impedance at the ground rod? Does anyone understand the theory of a clamp on tester?
I assume you are using an AEMC loop tester. It simply injects a current into a loop then reads the voltage derived from the impedance @ the test frequency (1689 Hz). There is a certain amount of skill and/or knowledge required to use the instrument.
The main purpose is to get a general idea (verification) of ground rod impedance formed by the loop created by the utility ground rod at the transformer, the grounded service conductor between the transformer and service disconnect, the GEC, earth, and the ground rod under test. However it is only a ball park figure and always reads higher than actual value.
Example: If we clamp around any grounding electrode in a multi-grounded system (more than one rod), the measured value of the electrode under test will be the resistance of that particular rod in series with the equivalent parallel resistance value that the rest of the multi-grounded system represents. If we had 4 grounding electrodes and each a resistance value of 25 ohms and we were to clamp around any electrode in the system, the measured value would be 25 ohms in series resistance of 8.33 ohms giving a total of 33.33 ohms.
Moving on from there the only real purpose you could use the meter for is verifying continuity between points. Once you get past the service and start reading cable inside, all you are reading is hard loops and verifying continuity between points. Example: take a 50 foot piece of wire, lay it out, and join the two ends together. The meter will indicate .7 ohms every time or a shorted loop. It only verifies continuity, but does not tell the impedance because it only goes down to .7 ohms. It takes a very special high dollar DLRO to read any resistance lower than 1 ohm.
So IMO the loop tester is only good for verification of Pole Grounds, Transmission Tower Grounds, Transformer Grounds, Phone Pedestal Grounds, Service Grounds, and verifying continuity of loops.
To actually measure earth impedance of a ground electrode systems you need a three-point, or four-point "fall-of-potential method.
As for what should the ground impedance should be is undefined by NEC. It only requires a single rod, pipe, or plate that does not have a resistance of 25 ohms or less shall be augmented by one additional electrode of any of types specified by 250.52(A)(2). So if one rod produces say 500 ohms, you are only required to add another rod which should give you 250 ohms. The 2 ohms you quoted are specifications used by some industries, not any NFPA requirement.