"Grounds for Grounding", Joffe and Lock, IEEE Press, has a whole section regarding control of ESD in facilities (Section 10.3). This is an excerpt from 10.3.5 regarding connection of the ESD ground to the building safety ground.
Design and construction of ESD protected areas is commonly achieved through grounding ESD protective equipment in a two-step procedure. The first step is to en* sure that everything in the work space is maintained at a common electrical potential at all times during normal operation. This is achieved by grounding all components of the work area, including all BSD protective elements such as external parts, work surfaces, personnel, and electronic test equipment and power tools in an electronics production and test area, to the same electrical ground point called the common-point ground {31, 32]. This ESD common-point ground should be properly identified. Use of the symbol in Figure 10.31 is recommended to identify the common-point ground. Figure 10.32 shows a practical implementation of ESD common-point grounding [29].
The second step for achieving ESD protective grounding is to connect the common point ground to the local equipment electrical safety ground (ESG) or protective earth (PE) connection point. This is the preferred ESD ground connection because all electrical equipment on the site should already be connected to this point. Connecting the BSD control materials or equipment to the equipment electrical safety ground guarantees that all components in the work space are at the same electrical potential. If this were not the case, a possible electrical potential difference between the electrical safety ground (to which the ESDS item is connected) and an auxiliary ground (to which the work space surface containing the ESDS item was to be connected) could result in damage to the ESDS item, counteracting the purpose of the ESD ground and possibly even constituting a safety hazard for personnel if they come into electrical contact with both grounding systems simultaneously. Subsequently, any auxiliary ground structures (e.g., water pipe, building frame, or ground stake) present and used in the work space must be bonded to the equipment electrical safety ground in order to maintain the integrity of the connections from the common-point ground to this point and to. Minimize electrical potential differences between the two. The resistance between the two connections should be as low as possible, typically less than 1 ohm.
Figure 10.32. Implementation of ESD common point ground. (Image courtesy of M. Netzer.)