For a good background in static electricity, see NFPA 77. Storage cabinets are typically not grounded since static electricity is not generated during storage. Of course this only applies to the containers in the cabiinet and if there is dispensing of any kind it is no longer storage. Personnel can become charged simply by walking across the floor and by other activities, and may need preventive measures. A charged person approaching a cabinet or container at a different potential, grounded or not, can create a spark. If you can see it or feel it, it is probably incendive and capable of igniting a combustible vapor/gas in air when within the flammable limits. Grounding for static dissipation should be less than 1 megohm (!) to ground and any wire you can buy, even 40 AWG, will be of sufficient ampacity. Assuring mechanical integrity, however, requires something more robust.