chrisreisinger79
Member
- Location
- Grand Rapids, MN, USA
Would a permanently secured 1/4hp 120vac fan be considered a stationary motor and thereby fall under 430.109(C)(1) for disconnecting purposes?
430.109(C)(1) is what permits him to use a general use snap switch for motors 2hp and under / 300 volts and under.As I interpret your question, yes. This is the definition of "stationary", as opposed to one with a cord and plug. The issue is, the cord and plug can serve as the disconnecting device, but if it is "stationary" as in permanently wired, then you must provide a disconnecting means. But that can be a suitably rated snap switch.