Looking at 430.24 and 440.22
How did the manufacture come up with 18.9 min Circuit ampacity. The compressor Rla 14.1
Fan motor fla 1with a 1/6 hp motor table fla of 2.2
The manufacture took 14.1 rla × 1.25 =17.625.
The manufacture did not use the table fla of 2.2instead took the motor fla of 1fla.looking at 430.24 this confused me at first because the manufacture took the smaller fan motor fla of 1 × 1.25.
1.25 + 17.625 = 18.875
18.9 min Circuit ampacity
Anyhow I found it to be interesting how the manufacture applies article 430.24
As a side note say the compressor motor is 2hp with a rla of 14.1 @ 230 volts the table fla is 12fla
So you have a motor with a fla of 12fla under normal conditions. But because it is a compressor and the motor is being cooled it has a fla of 14.1 being identified as rla.
Ii also found it interesting that the term fla was changed in 1972 to rla for compressor article 440 motors
How did the manufacture come up with 18.9 min Circuit ampacity. The compressor Rla 14.1
Fan motor fla 1with a 1/6 hp motor table fla of 2.2
The manufacture took 14.1 rla × 1.25 =17.625.
The manufacture did not use the table fla of 2.2instead took the motor fla of 1fla.looking at 430.24 this confused me at first because the manufacture took the smaller fan motor fla of 1 × 1.25.
1.25 + 17.625 = 18.875
18.9 min Circuit ampacity
Anyhow I found it to be interesting how the manufacture applies article 430.24
As a side note say the compressor motor is 2hp with a rla of 14.1 @ 230 volts the table fla is 12fla
So you have a motor with a fla of 12fla under normal conditions. But because it is a compressor and the motor is being cooled it has a fla of 14.1 being identified as rla.
Ii also found it interesting that the term fla was changed in 1972 to rla for compressor article 440 motors