The other day, I was asked to determine why the breaker for a recently installed combination whirlpool tub and steam shower unit was tripping within a minute or so of activating the steam function. I took an amp reading at the 20 amp breaker that was tripping. It was drawing 1.7 amps with only the lights on. When the steam function was activated, the load became 28 amps. I asked the homeowner for documentation on the unit. The installation guide shows, the steam generator is rated at 3kw. I told the homeowner, this requires a 30a circuit. Upon examination I found that there was a factory attached cord & plug. The cord was 12awg and the plug was a standard 15a blade configuration. I am reluctant to run a 30a circuit to plug this steam unit into. Opinions please 