Steam Shower Installation – Attic Access & Wiring Dilemma
Good afternoon everyone,
I have a bit of a dilemma and could use some advice.
I’m installing a steam shower unit in a second-floor single-family home, with the attic access being the intended installation location. However, the main panel is on the first floor, and due to the layout, running conduit or smurf tube directly to the unit would exceed the NEC’s 360-degree bend limitation.
The steam shower requires 55A at 240V.
I originally considered running 6/4 Romex, but I’m aware that the ampacity of NM-B cable is not the same as individual conductors rated per Table 310.15(B)(16). Since Romex is limited to the 75°C column, it wouldn't meet the ampacity requirement for this load.
Given the conduit restrictions, would it be permissible to run SER cable for this branch circuit to feed the 55A two-pole steam shower unit? If so, what size would be appropriate?
I appreciate any guidance on this. Thanks in advance for your help!
Good afternoon everyone,
I have a bit of a dilemma and could use some advice.
I’m installing a steam shower unit in a second-floor single-family home, with the attic access being the intended installation location. However, the main panel is on the first floor, and due to the layout, running conduit or smurf tube directly to the unit would exceed the NEC’s 360-degree bend limitation.
The steam shower requires 55A at 240V.
I originally considered running 6/4 Romex, but I’m aware that the ampacity of NM-B cable is not the same as individual conductors rated per Table 310.15(B)(16). Since Romex is limited to the 75°C column, it wouldn't meet the ampacity requirement for this load.
Given the conduit restrictions, would it be permissible to run SER cable for this branch circuit to feed the 55A two-pole steam shower unit? If so, what size would be appropriate?
I appreciate any guidance on this. Thanks in advance for your help!