Steel conduit with bare grounding conductor

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Does a steel conduit containing bare copper grounding conductor require bonding per NEC?


Enviado desde mi iPhone utilizando Tapatalk
 
Is it a GEC or an EGC? A GEC would require bonding whether it's bare or insulated.

It’s actually part of the equipotential bonding grid - not really an electrode but it’s all over the place
They’re using it to bond equipment and stubbing up with RGS and bare grounding conductors


Enviado desde mi iPhone utilizando Tapatalk
 
What about the magnetic choking effect if there is a fault to the grid?



Enviado desde mi iPhone utilizando Tapatalk
That would only apply to a GEC. You said it was for bonding equipment which would not be part of the GES.
 
That would only apply to a GEC. You said it was for bonding equipment which would not be part of the GES.

But the ground loop is tied to the electrode system - ground rods so it’s not really possible to separate the two


Enviado desde mi iPhone utilizando Tapatalk
 
What in the NEC would require that if the conductor within the raceway is not a GEC? Besides that any fault should be returning on the EGC.

It’s not required to be in a conduit but that’s the way it was designed
MOST of the fault current will travel via the EGC…but not all of it.


Enviado desde mi iPhone utilizando Tapatalk
 
Correct so you’d have at least two paths for a fault current to flow: One of very low impedance via the EGC and another via the ground loop of much higher impedance.


Enviado desde mi iPhone utilizando Tapatalk
Which is always the case and would not affect the GEC.
 
Which is always the case and would not affect the GEC.

Yes we agree - but what does that have to do with bonding the steel conduit with bare bonding conductors?
If we don’t have to do it per NEC that’s great. But it seems like they should be bonded


Enviado desde mi iPhone utilizando Tapatalk
 
I don't think it needs to be bonded per NEC and I don't think there is any choke effect to worry about for a stub.

Thanks , I’ll go with that But,
If the grounding cable were routed in a long conduit run vs just a stub up would that make a difference?