I have a project in which we are rewiring a 12 unit apt complex. The engineered drawings call for us to replace the single phase 240/120 sub-panel yet calls for the sub-feed to remain existing. The existing sub-feed is a 125A feed consisting of (3) 1/0 aluminum conductors in a steel flex conduit. I have landed this in our new panels and installed a ground bushing from the flex connector to our panel ground bus bar. I am not sure if there is a violation in place. Drawings call for sub-feed to remain existing. Can the inspector require us to attempt to pull in a ground conductor or is ok to let steel flex remain the pathway.
 
Is the wiring method Steel MC, AC or Flexible Metal Conduit?
"Steel Flex" is not specific enough, as steel MC or AC would be allowed.
 
I have a project in which we are rewiring a 12 unit apt complex. The engineered drawings call for us to replace the single phase 240/120 sub-panel yet calls for the sub-feed to remain existing. The existing sub-feed is a 125A feed consisting of (3) 1/0 aluminum conductors in a steel flex conduit. I have landed this in our new panels and installed a ground bushing from the flex connector to our panel ground bus bar. I am not sure if there is a violation in place. Drawings call for sub-feed to remain existing. Can the inspector require us to attempt to pull in a ground conductor or is ok to let steel flex remain the pathway.

The "flex" portion would need to be specifically rated as suitable for being an EGC.
 
Read 250.118 (5). Overcurrent Device not to exceed 20 amps. Combined length of conduit not to exceed 6 feet.
 