Dark Sparky
Member
- Location
- USA
- Occupation
- Electrical Engineer
In this thread:
http://forums.mikeholt.com/showthrea...ht=egress+step
Charlie mentions:
"If you were to draw lines on the floor to depict the required working clearances around all the equipment in the area, would there be space on this level that is not within the lines? In other words, can you be standing within the working space in front of any of the equipment, and walk out of the working space, and still be on the same floor level? If so, the manner of egress from that point to the outside world is not within the scope of the NEC. All the NEC cares about is that you can safely leave the designated working space."
We have a scenario where we need to put some electrical equipment (MCCs, panels) all in a row on a raised platform. Once you are away from & off of this electrical platform, the rest of the area will be a (one) step down. In the above thread, Charlie mentions that one needs to be able to "walk out of the working space." I'd like some interpretations on the code requirements for our platform's size. I am unsure if the platform needs to ONLY be the size (width and depth) of the 110.26 "Working Space", or if it needs to be this size PLUS some amount so that one can step out of the working space, and still be on the same level? Or maybe there is some other proper code-mandated size. Hopefully I am clear. If the platform needs to be larger than the Working Space, how much larger?
FYI for context, this is in an interstitial space between a walk-on ceiling and a roof. Because we have the MCC, panels & transformer, the walk-on ceiling can't support their weight. Thus we will design a platform (steel grating?) to hold the electrical equipment. Because the platform needs depth (structurally), it will create an area (working space?) around the panels, from which one will need to step down.
Thank you in advance for your time and opinions.
http://forums.mikeholt.com/showthrea...ht=egress+step
Charlie mentions:
"If you were to draw lines on the floor to depict the required working clearances around all the equipment in the area, would there be space on this level that is not within the lines? In other words, can you be standing within the working space in front of any of the equipment, and walk out of the working space, and still be on the same floor level? If so, the manner of egress from that point to the outside world is not within the scope of the NEC. All the NEC cares about is that you can safely leave the designated working space."
We have a scenario where we need to put some electrical equipment (MCCs, panels) all in a row on a raised platform. Once you are away from & off of this electrical platform, the rest of the area will be a (one) step down. In the above thread, Charlie mentions that one needs to be able to "walk out of the working space." I'd like some interpretations on the code requirements for our platform's size. I am unsure if the platform needs to ONLY be the size (width and depth) of the 110.26 "Working Space", or if it needs to be this size PLUS some amount so that one can step out of the working space, and still be on the same level? Or maybe there is some other proper code-mandated size. Hopefully I am clear. If the platform needs to be larger than the Working Space, how much larger?
FYI for context, this is in an interstitial space between a walk-on ceiling and a roof. Because we have the MCC, panels & transformer, the walk-on ceiling can't support their weight. Thus we will design a platform (steel grating?) to hold the electrical equipment. Because the platform needs depth (structurally), it will create an area (working space?) around the panels, from which one will need to step down.
Thank you in advance for your time and opinions.