Can I come out of the 480 /208 -120 transformer in to 2 fused disconnects (100 Amp each) or I have to terminate in one 200 Amp fused disconnect and than feed each 100 Amp separately?
Can I come out of the 480 /208 -120 transformer in to 2 fused disconnects (100 Amp each) or I have to terminate in one 200 Amp fused disconnect and than feed each 100 Amp separately?
I agree with david but might add you need to be sure that you maintain your transformer protection by properly sized overcurrent devices, primary or secondary, per 450.3 (see Table 450.3(B) + the notes)