SkeeterFLA
New member
- Location
- Afghanistan
New to the forum, but I need some assistance. We have European 220v 50Hz single phase as our shore power. We have an outdoor rated mechanical step down transformer (Acme) to get to 110v for U.S. equipment. From the xfmr we are feeding a UPS (APC BE650G1) for equipment back up. Trouble is, the trouble light on the UPS "Building wiring fault" stays on. When we tested the transformer output, the tester indicated "open ground".
Everything is wired correctly and xfmr case is grounded to electrode.
However, if we use an indoor rated step down xfmr, there is no trouble indicator light.
Any ideas?
Everything is wired correctly and xfmr case is grounded to electrode.
However, if we use an indoor rated step down xfmr, there is no trouble indicator light.
Any ideas?