step down xfrm

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
use a 480 x 120/240 single phase transformer and connect it to two of the 480 volt conductors.

The entire panel load will then be on one of the three line-to-line phases, but as long as the imbalance is OK, it meets the OP's request.

Distributing the single phase load across all three service phases requires a Leyton hookup.
 