We have a Step Up 75KVA transformer 208 to 480V, configured Delta-Wye, feeded from a 150A sub-feed 3-phase breaker in a panel 42 ft away.
The secondary load is an equipment panel with a 100A 3-phase main disconnect, 10ft away from the transformer. No neutral.
Do we need a disconnect for the transformer?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
We have a Step Up 75KVA transformer 208 to 480V, configured Delta-Wye, feeded from a 150A sub-feed 3-phase breaker in a panel 42 ft away.
The secondary load is an equipment panel with a 100A 3-phase main disconnect, 10ft away from the transformer. No neutral.
Do we need a disconnect for the transformer?
You always need a disconnect for a transformer. But it does not have to be anything other than the feeder breaker in most cases.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
450.14 Disconnecting Means. Transformers, other than Class 2 or Class 3 transformers, shall have a disconnecting means located either in sight of the transformer or in a remote location. Where located in a remote location, the disconnecting means shall be lockable in accordance with 110.25, and its location shall be field marked on the transformer.
 

Charlypt

Member
Location
Florida
Occupation
Electrician
My confusion is about 240.21(C)(1):

(1) Protection by Primary Overcurrent Device. Conductors
supplied by the secondary side of a single-phase transformer having
a 2-wire (single-voltage) secondary, or a three-phase, delta-delta
connected transformer having a 3-wire (single-voltage) second-ary,
shall be permitted to be protected by overcurrent protection
provided on the primary (supply) side of the transformer, provided
this protection is in accordance with 450.3 and does not exceed
the value determined by multiplying the secondary conductor
ampacity by the secondary-to-primary transformer voltage ratio.
Single-phase (other than 2-wire) and multiphase (other than
delta-delta, 3-wire) transformer secondary conductors are not
considered to be protected by the primary overcurrent protective
device.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It seems that a wye-wye transformer would be likewise protected as virtually three two-wire 1ph units.

Is it not because secondary line-to-line loads can somehow cause higher primary line currents?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
My confusion is about 240.21(C)(1):

(1) Protection by Primary Overcurrent Device. Conductors
supplied by the secondary side of a single-phase transformer having
a 2-wire (single-voltage) secondary, or a three-phase, delta-delta
connected transformer having a 3-wire (single-voltage) second-ary,
shall be permitted to be protected by overcurrent protection
provided on the primary (supply) side of the transformer, provided
this protection is in accordance with 450.3 and does not exceed
the value determined by multiplying the secondary conductor
ampacity by the secondary-to-primary transformer voltage ratio.
Single-phase (other than 2-wire) and multiphase (other than
delta-delta, 3-wire) transformer secondary conductors are not
considered to be protected by the primary overcurrent protective
device.
It seems your question is about the secondary conductors and not the transformer. Look at the other paragraphs in 240.21(C). Your installation is allowed.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Do you find it curious that a local transformer disconnect is not explicitly required to be lockable?
NFPA 70E and agencies like OSHA cover LOTO.
My opinion is the NEC locking provisions go beyond its intended scope of not duplicating other standards. But I appreciate how having fixed in place provisions installed makes complying with other standards easier.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
It seems that a wye-wye transformer would be likewise protected as virtually three two-wire 1ph units.
Agreed, assuming you mean the secondary conductors supplied by a wye-wye transformer would be likewise protected by the primary OCPD.

Is it not because secondary line-to-line loads can somehow cause higher primary line currents?
As far as I can see it's either an oversight, or an omission for simplicity on the basis that wye-wye transformers are seldom used for NEC applications.

Cheers, Wayne
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
The Brit here again. My field is industrial power electronics. We rarely, if ever, use step-up transformers. Often we 11 kV down to 700 DC. Specials for us. Regular systems are just 400Vac.
 