We have a client that needs to step up voltage from 208 to 480, the compressor fla is 78 amps. I calculate that the run current on the primary would be about 185 amps. What would the start up current be? Thanks John
You already have pretty good answers on your specific question. Nothing else I could add..
Following is based on the xfm will be feeding only the motor - dedicated xfm.
And there are issues with transformers dedicated to a single motor load. primarily transformer energization inrush current, motor inrush and LRC, Voltage drop at the motor during starting.
What size transformer are you looking at? 480V, 3ph, 78A is 65kva. If you are looking at a 75kva, consider the voltage drop. At locked rotor the VD could easily be 30+%. If this is a package unit with a non-nema motor that could easily be a problem. As already suggested, definitely get the mfg motor inrush and LRC data.
Consider a 150kVA, 208D/480Y. This will cut the voltage drop during motor starting in half - The motor will like that.
For a 150KVA, primary (208) FLA is 416A, xfm inrush is as much as 10X, say 4000A.
I don't know the capacity of the 208V system, but you definitely want the transformer on all the time - minimize xfm energizatons. I highly suspect xfm energization will severly blink the lights - and everything else.
With the information we have, I'd select the primary CB at 125% FLA, next size up, 600A, conductors just over 500A.
Without mfg data, consider the motor LRA at 6X, as already suggested - say 1000A on the primary. This will also blink the lights but not nearly as bad as the xfm energization. Delay the motor start for at least a few seconds after xfm energization.
Consider sizing the secondary conductors at 125% motor FLA. Terminate in a listed combination starter suitable for the motor. If it is a package unit, size the conductors to the CB, or MFG direction.
Just some random thoughts - hope it helped.