First, you can step 240v up to 277v with a buck-boost. But, why can't you just use the 240v?Does Square D / Schneider make a Step Up SINGLE PHASE Transformer with a primary voltage of 120/240v and a Secondary Voltage of 277/480v-1?
Sure you can. I found a 120v-to-277v lighting transformer.You can't get 277V without three phase.
No. This is a large warehouse with a 240/1 service but due to the size of the warehouse, I want to use 277v for the high bay lighting.
Sure you can. I found a 120v-to-277v lighting transformer.
That can happen here if you're not careful.Learned something new.
You can't get 277V without three phase.
No. This is a large warehouse with a 240/1 service but due to the size of the warehouse, I want to use 277v for the high bay lighting.
Not off the shelf but you could have a 120 primary to a 480v secondary with a 277v tap custom woundThat's why I asked, since you only need to go from 240-277 and not 480 you should be able to find a suitable 1Ø transformer. If you were searching for 1Ø, 240-277/480 transformer I don't think that you will find one without going to 3Ø.
Agreed. I don't see the problem.Not off the shelf but you could have a 120 primary to a 480v secondary with a 277v tap custom wound
Which leaves you with 203 volts on the other side of the tap - should only allow using 58% of the transformer kVA rating also unless you are able to connect some lights as 208 volt loads.Not off the shelf but you could have a 120 primary to a 480v secondary with a 277v tap custom wound
Why bother with the 480v winding if it's custom-made? I'd opt for 240v to 277v, whether standard, auto-transformer, or buck-boost.Not off the shelf but you could have a 120 primary to a 480v secondary with a 277v tap custom wound
Which leaves you with 203 volts on the other side of the tap - should only allow using 58% of the transformer kVA rating also unless you are able to connect some lights as 208 volt loads.
Yeah, I missed the 240v primary requirement. But then you could have a 240v to 480v with a 277v tap single phase xformer wound.
MGM Transformer in Los ANgeles does custom winds. But then there is the subject of listing. Not sure is a custom design is listed even if the manufacture has UL certification.
Do transformers need to be listed as a general rule? Some specific applications do.
Doesn't matter what the primary voltage is, if you have a 480 secondary with a 277 tap - you only get 58% of the VA rating of the transformer from that 277 tap - might as well have gone with a 277 secondary to begin with unless you have a use for the remaining 203 volts on the other side of the tap.