Re: Step Up Transformer
First of all we have not been told the rating of the load. Is it a 3-phase, 240/138 volt european equipment and is the neutral necessary? If the neutral is not needed, I believe the least expensive method to solve the 3-phase, 208V to 240V problem is to buy two single-phase transformers rated 208v primary and 32v secondary. Connect them in an open delta 3-phase boost configuration so that the input 208v plus the secondary 32v are additive and will provide 3-phase 240V without a neutral.
However, if a neutal is needed, you will have to use 3 single-phase, 208v primary with 32v secondary transformers connected in WYE to provide 3-phase and develop a 138 volt neutral.