jimsomers10
New member
- Location
- Reading, PA, USA
Recently I came across a question and I was stumped by it so I figured maybe someone else might know the answer. First I will give a little background information. I am dealing with a 3 phase 15KVA step-up transformer 208V:460V. The load on the secondary is 4300 VA. The transformer is rated for 41.69A on the primary side so with 125% protection it is 52.11A. The primary is being supplied by a 3 phase 60A breaker and the panel has plenty of room and will not be overloaded. The equipment that is being feed from the secondary has 15A fuses on each phase internally. According to Table 450.3 in NEC 2008, I do not need secondary protection for the TRANSFORMER, however according to article 240.4 F there needs to be overcurrent protection on the secondary for the conductors. Here is where my question comes in. Is article 240.4 F covered since there are internal fuses in the equipment or do I need to connect a fuse disconnect on the secondary conductors as well, and if so what size would you recommend. Thanks for all your help!