GG
Senior Member
- Location
- Ft.Worth, T.X.
Im trying to figure out how to repair this apartments meter base. Its a 4 gang meter base and someone cut the wires from the load side and stole the meter prong block that fed 1 apt. The inspector wrote that he wants new service wires pulled to the apartments inside breaker box which is inside the apt 80' away. Why not just use split bolts and add splices inside the meter base and install a new meter base prong block? Now the inspector wants new wire? I see several problems with this and here they are.
(1) The 4 gang meter base is not grounded to a cold water pipe or a ground rod. Conduits leave the bottom of the 4 gang meter base where they run under the slab and turn up inside each apt to a 125A panel.
(2) There are 3 wires feeding the apt's 125A panels and the panels do not have a main breaker. The neutrals are bonded to the grounds inside the breaker boxes. The conduit cannot be used as a ground path because the conduit is PVC in the slab.
(3) The conduit is 1 1/4" and too small to add a ground wire.
(4) The owner wants to run a new 4 wire cable through the attic but then he would need a 125A disco outside and if we do this then I have to seperate the grounds and neutrals inside the apt breaker box. If I do this then run a ground rod and CWG outside for my disco then what about the remaining 3 panels that still have there neutrals and grounds bonded inside? I need help and cant figure this one out. Thanks.
(1) The 4 gang meter base is not grounded to a cold water pipe or a ground rod. Conduits leave the bottom of the 4 gang meter base where they run under the slab and turn up inside each apt to a 125A panel.
(2) There are 3 wires feeding the apt's 125A panels and the panels do not have a main breaker. The neutrals are bonded to the grounds inside the breaker boxes. The conduit cannot be used as a ground path because the conduit is PVC in the slab.
(3) The conduit is 1 1/4" and too small to add a ground wire.
(4) The owner wants to run a new 4 wire cable through the attic but then he would need a 125A disco outside and if we do this then I have to seperate the grounds and neutrals inside the apt breaker box. If I do this then run a ground rod and CWG outside for my disco then what about the remaining 3 panels that still have there neutrals and grounds bonded inside? I need help and cant figure this one out. Thanks.