We are installing a new lineup of 4160V switchgear. The substation was bought from a major manufacturer and came with all provisions in place for the 125VDC power system, except the battery and charger which we decided to purchase seperately. The gear is metal-clad gear with a walk in aisleway and open areas at each end of the gear. The battery system, AC distribution panel and DC distribution panel are located in one of these open areas. The gear is currently set up with a thermostatically controlled ventilation fan. We are also planning to install a hydrogen gas monitor. The manufacturer used FMC in the substation for the entrances and exits from the distribution panels and for the battery system connections they had put in place for us to use.
During the install our electrical contractor pointed out NEC 348.12(3.)
We questioned the mfg and their response is that this is not a battery storage room.
Any advice on this application would be appreciated
During the install our electrical contractor pointed out NEC 348.12(3.)
We questioned the mfg and their response is that this is not a battery storage room.
Any advice on this application would be appreciated