Are these cabinets for storing flammable liquids ( wd40,paint thinners and others) considered to be in a classification .If they are or not should they at least be bonded.
Are these cabinets for storing flammable liquids ( wd40,paint thinners and others) considered to be in a classification .
probably not. in any case, why would there be any electrical equipment inside the paint storage cabinet?
If they are or not should they at least be bonded.
probably. But it is just a means of dissipating static so it does not have to be an especially large wire. If it is sitting on a bare concrete floor that might be adequate, although a green wire tied to the building structure might make everyone feel better.
While most of them have a bonding termination, there is no code requirement to bond them.
As far as I know, not in any of the codes or standards that apply to flammable liquid storage cabinets.Not in the electrical code anyway.
As far as I know, not in any of the codes or standards that apply to flammable liquid storage cabinets.