There is a storage container on a commercial site that needs a 20 amp 120V circuit for lighting to be installed in it.
It is a 50' metal rail car with a door cut in the side of it.
A 3/4" pvc conduit was installed between an exitsting metal building and the storage container. Roughly 50' between them.
There will not be any bonding between the existing metal building and the storage container other than the EGC that will be run with the single 120v circuit.
Is there any more bonding or grounding required at or between the storage container and the existing building ?
My thoughts are if the small EGC was somehow compromised between the 2, no return path would exist at all should a fault happen to occur.
JAP>
It is a 50' metal rail car with a door cut in the side of it.
A 3/4" pvc conduit was installed between an exitsting metal building and the storage container. Roughly 50' between them.
There will not be any bonding between the existing metal building and the storage container other than the EGC that will be run with the single 120v circuit.
Is there any more bonding or grounding required at or between the storage container and the existing building ?
My thoughts are if the small EGC was somehow compromised between the 2, no return path would exist at all should a fault happen to occur.
JAP>